Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

3 pole or 4 pole STS??

Status
Not open for further replies.

wonderchi

Electrical
Aug 24, 2006
36
0
0
AU
Hi,

Can someone clarify for me...when can we select a 3 pole STS over a 4 pole STS unit?

Thanks

Allan
 
Replies continue below

Recommended for you

Let me rephase my question:

I am to install a STS (static transfer switch), in the upstream we only have one supply and one generator...I am planning to use a 3 pole STS instead of a 4 pole STS...(since we dont need to switch the neutral because there is only one generator)...Am I right?

Please advise
 
The important point is not the number of generators, it is the number of connections to ground.
My preferred installation is as follows:
Supply to 3 pole transfer switch.
Generator to 3 pole transfer switch.
Solidly connected neutrals.
From the transfer switch to the main panel.
One connection from neutral to ground in the main panel.

The code only allows one connection from the neutral to ground. There are very good reasons for this.

If for any reason, there must be more than one ground on the neutrals then the neutrals must be switched in such a manner that only one at a time is ever connected.

There may be some exceptions to the "one ground connection" rule if more than one building is involved.
respectfully
 
Status
Not open for further replies.
Back
Top