Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

3" DIA x 6" CONCRETE TEST CYLINDERS

Status
Not open for further replies.

PT999

Structural
Oct 3, 2002
150
I am seeing these smaller concrete test cylinders being used to mold concrete for compressive strength vs the traditional 6" dia x 12" high test cylinder molds

Is this permitted by ACI
 
Replies continue below

Recommended for you

4x8's are now permitted by aci and ibc. you should read the documentation though since it requires more specimens and possibly different equipment.
 
I would guess you are seeing 4"x8" cylinders rather than the 3"x6" in the thread title. As msucog pointed out, ACI standard strength acceptance is based on 2 - 6"x12" cylinders or 3 - 4"x8" cylinders at 28-days. No matter what, you are still limited to 3x the maximum aggregate size of the aggregate in the concrete per ASTM C 31, and the consolidation procedure is 2-lifts with a 3/8" diameter rod. The 4"x8" cylinders can only be used for concrete containing aggregates up to 1 1/4" maximum size.

Greg
 
Status
Not open for further replies.