kmh1
Electrical
- Sep 12, 2003
- 47
I am working with an application where an individual is planning to connect a 256 kW, 600 volt three phase induction generator to the utility grid via a 600/4160 volt step up transformer. The transformer installed is HV wye - LV delta and the desire is to install a 3 conductor armoured 5kV cable for the utility connection. The utility is considering the need for a neutral connection to the transformer wye point (i.e. 4 conductor cable) but I believe the wye connection could be left ungrounded in this case as the induction generator would simply provide balanced 3-phase power to the grid and could never operate islanded without any excitation. Single phase loads would be serviced by the utility side 4-wire distribution transformer connected to the 4160 volt system. Does anyone see any problems with this scenario?