Just wondered if anyone can offer some analysis on the following configurations for a 3-wire transmitter circuit? I have recently been presented with an unfamiliar configuration whereby the sensor 0V is distributed back on two leads resulting in a pseudo 3 wire arrangement using 4 lead wires in total (see Figure 1).

In my previous experience with 3 wire configurations the 0V terminal has one connection. I'm attributing this to bad design as my gut feeling is there is something wrong with this circuit but I can't explain why. I'm thinking there could be issues with potential differences in signal ground but I'm stuck.

Can anyone offer some analysis?
 
 http://files.engineering.com/getfile.aspx?folder=2b4eb4f8-9833-4bca-8af7-6f5338406189&file=Figure_1_-_3w_loop_configurations.png
Replies continue below

Recommended for you

You can use the
ice_screenshot_20160718-141231_fehckj.png
so everyone doesn't have to clickclickclicketc

Figure_1_-_3w_loop_configurations-1_xmq2oe.jpg


I'm guessing but the 'A' seems to cancel the wiring voltage drop from the supply which might otherwise affect the signal.

Keith Cress
kcress -
 
Configuration A is better don't you think it doesn't suffer Voltage drop caused by the excitation current for the transmitter.
 