- Apr 22, 2004
- 6
We have a cooling system problem where 60 degree cone type fittings are leaking. We have systems that do not leak, and the common factor appears to be Ethylene Glycol in the systems that leak. The coolant is de-ionised water at about 0.5uS/cm.
I have heard that both de-ionised water and glycol are "searching" liquids that will find their way out. The leaky systems are showing carbon deposits on the conductivity probe (carbon electrodes), to the extent that the probe gap was bridged competely. The pump seals are leaking and are a standard carbon loaded type, which I have also since found out is a no-no for de-ionised water as it leaches the carbon (antimony loaded seals are preferred).
We are looking at two options. Either remove the Glycol, or change the steel to steel cone fittings.
Does anyone have some words of wisdom on this?
I have heard that both de-ionised water and glycol are "searching" liquids that will find their way out. The leaky systems are showing carbon deposits on the conductivity probe (carbon electrodes), to the extent that the probe gap was bridged competely. The pump seals are leaking and are a standard carbon loaded type, which I have also since found out is a no-no for de-ionised water as it leaches the carbon (antimony loaded seals are preferred).
We are looking at two options. Either remove the Glycol, or change the steel to steel cone fittings.
Does anyone have some words of wisdom on this?