echap
Electrical
- Dec 28, 2004
- 3
We are doing a project here that will have (2) 4,000A 480/277V 3PH 4W dry type indoor substations. The primary voltage is 12,470/7200V 3PH 4W. We are planning an S&C PMH-12 pad mounted switch for the main service switch called "PS-1". The building owner will own this switch. Out local utility distributes in 4W (WYE type configuration).
My question is, would it be appropriate to bring 3 wires (Delta) from the main service switch (PS-1) (leaving the utility Neutral behind at PS-1) and have a Delta-Wye dry type substation transformer connection?
The transformers in the substations would be 2500AA/3333FA KVA VPI-Polyester air cooled. The substation secondary would be 4000A, 100% rated bolted pressure switch with GFI protection at 480/277V 3PH 4W.
Thanks,
Eric
My question is, would it be appropriate to bring 3 wires (Delta) from the main service switch (PS-1) (leaving the utility Neutral behind at PS-1) and have a Delta-Wye dry type substation transformer connection?
The transformers in the substations would be 2500AA/3333FA KVA VPI-Polyester air cooled. The substation secondary would be 4000A, 100% rated bolted pressure switch with GFI protection at 480/277V 3PH 4W.
Thanks,