345kv/138kv wye connected autotransformer with 34kv delta tertiary.
34kv tertiary has 3 wye connected 300/1 pt's and 2 34kv/240-120v open delta station service transformers.
Transformer was energized for the first time from the 345kv gcb with open 138kv breaker.
Approx 10 sec later, xfmr tripped via 87T.
Found LA's on 34kv phase b and phase c destroyed. Further inspection found that phase b and phase c of the 34kv pt secondary were shorted via an errant jumper. Jumper was upstream of the sec fuses.
Question: Presuming an overvoltage caused the arrestor failures, why was there an overvoltage to begin with as a result of the pt secondary being shorted between two phases. As noted above arrestors on phase b and phase c were destroyed, and phase b and phase c pt secondary were shorted.
Any and all thoughts are appreciated.