hrc
Electrical
- Nov 8, 2001
- 104
I've instigated some other discussions on these forums related to power factors and also sizing out of 3phase transformers related back to single phase loadings. But in some discussions, a few things are not quite clear.
The situation is this: I have a 208Y 3phase PDU, typical that is used all over the place in the states. This allows me to use either 208VAC (2 legs of the 3phase) or 120VAC (leg to neutral of course) to deliver to a bank of switching power supplies (this is a large network switch rack)so of course, the best design approach would be to try and put the same load one each pair of 208. Putting that aside, lets say we have 9 500W supplies, and each have a pf of .95 (just for reference). For a ballpark approximation, the simple relationship of P/V gives us 2.4A apparent draw for each supply. Adding in the pf value, gives the 'real' draw of 2.53A (correct?). IF we put a balanced load, each pair then would be seeing a load of approx 7.6A draw.
Now the end user is coming back and saying....you have a load of 4500W, and using the formula of I=W/(v*pf*1.73) is saying you only have a loading of 13A but I contend this is wrong because we don't have a pure 3phase load. If he wants to size out the transformer, he needs to use it based on the 7.6A * 3 = 22.7A total load, thus solving for watts he needs based on the 22.7A total load. This gives 7760 watts, and /3 would be 2.6KvA transformer.
Am I correct on this or is he correct?
The situation is this: I have a 208Y 3phase PDU, typical that is used all over the place in the states. This allows me to use either 208VAC (2 legs of the 3phase) or 120VAC (leg to neutral of course) to deliver to a bank of switching power supplies (this is a large network switch rack)so of course, the best design approach would be to try and put the same load one each pair of 208. Putting that aside, lets say we have 9 500W supplies, and each have a pf of .95 (just for reference). For a ballpark approximation, the simple relationship of P/V gives us 2.4A apparent draw for each supply. Adding in the pf value, gives the 'real' draw of 2.53A (correct?). IF we put a balanced load, each pair then would be seeing a load of approx 7.6A draw.
Now the end user is coming back and saying....you have a load of 4500W, and using the formula of I=W/(v*pf*1.73) is saying you only have a loading of 13A but I contend this is wrong because we don't have a pure 3phase load. If he wants to size out the transformer, he needs to use it based on the 7.6A * 3 = 22.7A total load, thus solving for watts he needs based on the 22.7A total load. This gives 7760 watts, and /3 would be 2.6KvA transformer.
Am I correct on this or is he correct?