Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

400/5 CT accuracy class and burden selection

Status
Not open for further replies.

incognito1

Electrical
Feb 25, 2016
25
could you pls let me know how to select accuracy class value and burden for a particular application of CT of 400/5?

i have 2 CTs of 400/5. one is accuracy class of 0.5 and another one with accuracy class 1.

and i can choose of the burdens from 1.5, 2.5 and 5VA for any CT.

how can i select accuracy class and burden for a 400/5 CT?
 
Replies continue below

Recommended for you

Metering? Protection? Electro-Mechanical relays? Digital relays? Moving disk meters? Electronic meters? Burden? Resistance of wiring?
It depends.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
CTs will be used for ELR, EFR, OCR under measuring and CTs will be used for measuring.

can you provide any selection criteria?
 
You'll have to do some basic design - secondary cable sizes, fault levels, relay burdens, secondary current, etc all interact. Start with what you can't control much, like fault level and relay burden, then see whether you can evaluate what the CT requirements are to drive the loop. Or if the CT is pre-determined then you might need to select the cable to suit.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor