400 CFM per Ton

Status
Not open for further replies.

Hileg

Electrical
Oct 8, 2003
24
A rule of thumb in air conditioning work is that 400 cfm of air is equal to 1 ton. If 400 cfm of air and a delta T of 20 degrees is achieved, this is equal to only 400X20X1.08=8640 btu/h.. This is not 12000 btu's. What am I missing here besides a college education.
 
Replies continue below

Recommended for you

You are neglecting the latent heat portion of the cooling load. The equation you quoted is for sensible heat. The latent heat (3360 btu/hr) is absorbed at the coil by condensing moisture from the air.
 
You should use the equation

Q = 4.5 x cfm x Delta h

to get total heat

HVAC68
 
Hvac68 is delta h enthalpy.
Thank you, this really helps.
 

The factor 1.08 reflects only sensible heat and is the product of

60 min/h * 0.075 lbm/CF * 0.24 Btu/(lbm*oF)​

which when multiplied by X CFM results in

X * 1.08 Btu/h​


 

A small correction to my last paragraph, it should say: when multiplied by X (CFM) * [Δ]T (oF) results in

X*1.08*[Δ]T Btu/h​
 