400 vs. 350 Amps Circuit Breaker 2

Status
Not open for further replies.

BGD011

Mechanical
Apr 2, 2004
32
We do have a 200Hp/460V/3ph/60Hz motor. The NEC tells me that the size of the circuit breaker (CB) should be 350 Amps. If we use a 400 Amps CB, is it violation of the NEC?
FLA of this motor is 240 Amps.

Thank you indeed in advance!
 
Replies continue below

Recommended for you

Which part of NEC tells you that? Is this a VFD?
NEC would allow up to 250% of the FLA rated CB. Look up Table 430.52 in NEC 430.
 
Thank you Rbulsara!

I see it now at that 2005 NEC table 430.52 last column.
The motor is not on the VFD but there is an auto transformer starter. I was not sure what it is the maximum rating for these CB’s,... Thanks again!
 
The Project I am working on; we are using a 400A Thermal-Magnetic (Inverse time) circuit breaker as stated in the Table 430.52 far column. According to the code we could use 2.5 *240FLA = 600A but we have chosen a 400A with a trip setting of 7.5X or 3000A which is 12.5 X FLA. The Motor Short Circuit Protector NEC Reference 430.52 (7) can have a trip setting of no more than 1700% FLA for high efficiency motors which we chose 1250% for the energy efficient motor loads. The Motor Overloads will protect the motor and cable in the event of a overload condition. We are using a 3/C 350 kcmil cable which is good for 310A at 75 deg C according to Table 310.16. This exceeds the 1.25 * (240)FLA = 300A that is required per the continuos Duty requirement 430.22 (a).

 
Thank you JBUDA54!
It is helpful information.
 