400Hz motor-generator and solid state frequency converter maintenance

Status
Not open for further replies.

jshindo

Electrical
Jan 5, 2011
1
I'm looking for information regarding maintenance and operation costs of motor-generator (MG) sets and solid state frequency converters (SSFC).

1. How often do I need to do maintenance on MG and SSFC?
2. How much will it cost?

Is there a ballpark number I can use in a lifecycle cost worksheet to present to an energy manager?
 
Replies continue below

Recommended for you

Do not expect any precision in the answers you get if you don't specify better than what you did.

A rotary set needs inspection (vibration monitoring and regreasing) at least a couple of times each year. If the unit is important, you may need to do it more often.

A solid state frequency inverter does not need any maintenance as such.
If there are fans, you need to change the fan regularly. Normal running time is a couple of years.
If the unit is water cooled, you will need to look at filters, pumps, conductivity etcetera. How often? Depends on what the manufactorer says.

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 