Hello electrical engineers,
In one of our 415V motor feeder, there was an arc flash. Attached are the photos. Relay in incomer saw the fault current as 12kA in all 3 phases for 100ms and fault current disappeared before the relay can trip. We see the cable from main bus connector to SFU got damaged but the cable from SFU to main contactor is OK. Fuse of R, Y phase got damaged severely. SFU is found OK when we opened it. Motor outgoing cable, motor IR tests were OK. SFU IR test is also OK.
We are confused what could have caused the accident.
My doubts are,
In SFU incoming, Y phase lug is still in SFU and connected tight but the cable got disconnected. So when it got disconnected it might have caused an arc which turned into 3 phase fault?
Requesting your valuable suggestions/opinions. Thanks in advance!
Thanks,
Vijay
Thanks,
Vijay
In one of our 415V motor feeder, there was an arc flash. Attached are the photos. Relay in incomer saw the fault current as 12kA in all 3 phases for 100ms and fault current disappeared before the relay can trip. We see the cable from main bus connector to SFU got damaged but the cable from SFU to main contactor is OK. Fuse of R, Y phase got damaged severely. SFU is found OK when we opened it. Motor outgoing cable, motor IR tests were OK. SFU IR test is also OK.