Hi
Thanks everyone. The requirement is in India. The supply voltage is 415VAC,50Hz, whereas the motor name plate states 440VAC,60Hz,45Kw. The motor would be driving a vertical spindle assembly via a flexible coupling and worm gear (suitable for both 60Hz & 50Hz). The worm gear adapts the vertical assembly speed to the motor speed depending on the worm gear ratio & can be operated at differential speed between 60Hz & 50Hz.
An earlier supply of the similar machine had a motor with a tag plate 415VAC,50Hz,45Kw and 440VAC,60Hz,52Kw, whereas the new supply has motor tag plate only states 440VAC,60Hz,45Kw, so the customer is the opinion that the motor is not suitable for the said machine. The motor power requirement for the machine is 45Kw max.
Also another query that VFD operating on a 415VAC,50Hz supply running a 440VAC,60Hz motor will reduce the life of VFD, as VFD has to compensate for increasing from 415V,50Hz to 440V,60Hz(motor). As per my understanding Since a VFD cannot increase the voltage above its supply voltage. Please advise.
Will also check posts by columbo7
Thanks
Bala