For an automatic transfer scheme in switchgear with SEL-351S relays connected to wye-wye incoming PT's on 34.5kV switchgear is there a need to monitor both 47N and 25 sync check functions on coming sources? sync check is required due to closed transition (there are also bus PT's) and a 47N is typically used for Neg Sequence. since 25 function is typically only monitoring one phase i'm assuming it cannot detect phase reversal or loss of phase on other two phases that is monitoring and thus 47N function is required?
Can a 59Q function be used in similar fashion to 47N (SEL-351 only has 59Q) and are there any pro's/con's to each?