dougjl
Electrical
- Sep 14, 2001
- 44
I have a question concerning the secondary side wiring. There are 4 taps X1, X2, X3 & X4. I know to get 240 I tie X2 & X3 together and get 240 between X1 & X4. Is there a problem grounding X4 and having 240 with a neutral? This would be similar to a 120 type arrangement and would seem to provide a safer system since a ground fault would trip the feeder breaker. If I wanted 120V couldn't I just pull that off of the X2/3 junction and still use X4 as the neutral? I know that typically the arrangement is to ground X2 & X3 (not X4) which then give 120 between X1 to X2/3 and X4 to X2/3 and take 240 from X1 to X4. Can someone explain why that is? What am I missing?
Thanks,
Doug
Thanks,
Doug