Had a three-phase transformer fail due to an arcing fault in the customer's switchgear. The fault occurred either at or ahead of the customer's 480 V main breaker. There was no other low side protection on the transformer since it was just a short distance between the transformer and the customer's switchgear.
The high side fusing eventually operated - but only after the transformer had failed. Fusing was set at 150% of transformer FLA and plots below (and to the left of) the transformer damage curve.
Customer claims the transformer fusing should have prevented the transformer from failing. My response is that the coordination between the fuse and tranformer damage curve only applies if it were a bolted fault condition. Am I looking at this wrong?
The high side fusing eventually operated - but only after the transformer had failed. Fusing was set at 150% of transformer FLA and plots below (and to the left of) the transformer damage curve.
Customer claims the transformer fusing should have prevented the transformer from failing. My response is that the coordination between the fuse and tranformer damage curve only applies if it were a bolted fault condition. Am I looking at this wrong?