enterprisenx12
Electrical
- Nov 13, 2014
- 5
Hi folks,
I have a 3-phase (3 pole wye connected) 480V circuit breaker that I need to supply three 200kVA single phase 480V identical loads (A-B, C-A, B-C). Only two legs are used for load.
As we know, in a balanced 3 phase system, the current across all three phases is kVA / 480V / sqrt(3). This means it would be 600kVA / 480V / sqrt(3) = 722A.
However, in this situation, I have 3 single phase loads (phase-phase), the current is 200 kVA / 480V = 417A.
A-B = 417A
C-A = 417A
B-C = 417A
What min ampacity should the three phase circuit breaker have to accommodate these loads? At least 722A or at least 417A? Note: Ignore the 125% sizing requirement for the moment.
I guess I am getting myself tripped up with how the upstream source ahead of the breaker sees these loads. I would expect in terms of kVA, the upstream source and thus breaker, sees 600kVA load. However, based on the single phase loads, it does not seem possible for each phase to be carrying 722A when I already showed that phase-phase 417A.
If I had to guess, the 722A min ampacity is the safest bet but really the sizing can be based off of 417A as its is not 3 phase - the current comes in one leg and retunrs on another leg. Just not sure then how you equate total kVA deman to total current demand when all of the loads are phase-phase and not phase-phase-phase or phase-neutral.
Can someone weigh in on this on wether 722A or 417A should be the basis? Please assume I need to configure the system this way with a single three phase (3 pole) breaker feeding phase-phase single phase loads.
Thank you all for your help!
I have a 3-phase (3 pole wye connected) 480V circuit breaker that I need to supply three 200kVA single phase 480V identical loads (A-B, C-A, B-C). Only two legs are used for load.
As we know, in a balanced 3 phase system, the current across all three phases is kVA / 480V / sqrt(3). This means it would be 600kVA / 480V / sqrt(3) = 722A.
However, in this situation, I have 3 single phase loads (phase-phase), the current is 200 kVA / 480V = 417A.
A-B = 417A
C-A = 417A
B-C = 417A
What min ampacity should the three phase circuit breaker have to accommodate these loads? At least 722A or at least 417A? Note: Ignore the 125% sizing requirement for the moment.
I guess I am getting myself tripped up with how the upstream source ahead of the breaker sees these loads. I would expect in terms of kVA, the upstream source and thus breaker, sees 600kVA load. However, based on the single phase loads, it does not seem possible for each phase to be carrying 722A when I already showed that phase-phase 417A.
If I had to guess, the 722A min ampacity is the safest bet but really the sizing can be based off of 417A as its is not 3 phase - the current comes in one leg and retunrs on another leg. Just not sure then how you equate total kVA deman to total current demand when all of the loads are phase-phase and not phase-phase-phase or phase-neutral.
Can someone weigh in on this on wether 722A or 417A should be the basis? Please assume I need to configure the system this way with a single three phase (3 pole) breaker feeding phase-phase single phase loads.
Thank you all for your help!