Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

480V/60A vs. 480V/100A

Status
Not open for further replies.

Cow44

Electrical
Joined
Feb 18, 2010
Messages
5
Location
US
Howdy,

Just found out that one tool we need in the shop will require 100 amps while the welder only requires 60A. If we wire all three 480v outlets to handle 100A then is it correct to assume the welder will be fine on these outlets as well? Thanks.
 
No problem functionally. I have seen this done many times. However, if this has to pass inspection it may be a judgement call for the inspector. My feeling is that most inspectors would overlook this but some may get sticky. If the welder has a suitable main breaker, (not just a main switch) and your cable is either within the limits for tap conductors or upgraded to 100 Amp rating, it will be easier for the inspector to pass or ignore the installation.
Put another way, if the welder has a main breaker and the cable is rated for 100 Amps your inspector will probably pass the installation.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
or buy a bigger welder... [wink]
 
Or hide the welder during the inspection...


Remember Peter, with great Power there must also come great Current squared times Resistance.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top