5.5kw 415v 3p >230v 1p atart and run capacitors
nick19851985
Industrial
Team I have a question, reasonable big motor to try and flick with steinmetz, 415v, 5.5kw, fla 8.9a, pf .9, eff 8.5, 50hz, 6.5 kvar,
I've done the maths and works out with going from wye to delta then to 1p, 26.6a drawn, with capacitors, slightly undersized with 120uf run and 320 uf start, run caps pull and extra 4.3a,
4mmtps cable which is 32 amps so right on the limit, have wired in a star delta starter to help with the start (hoping with the lower voltage to star will become like a soft starter aswell)
But if I stepped voltage from 230v to 460v which will have a voltage drop down a little, how would that fair on this system? Haven't installed yet, that's the question I'm a little baffled on as line>line is 415 3p and l>n is 230 3p which has is the same as supply so if I step up to 460v l>n (bit less slightly to small transformer) is that going to create and issue or will that and the circuit above work well?
Cheers
The same thing always happens.
Whenever you ask anything about a specific electric motor, first show its nameplate with the data at least.
For example, from your question it's not clear whether the 415V, 5.5 kW three-phase motor is designed to operate in a Wye or Delta connection.
I would love to but data plate is pretty beat up can read it but only just, not on a photo, that's why not shown in post, wye delta, 415 240 on air compressor with unloader and a pulsation dampener of such so happy to run in wye
Would rather do a star delta if I could thats why the question of step up of voltage, as l to l of 415 is 240, but since neutral is used as a somewhat phase in steinmetz can we get away with measuring a l to n on a delta at 415v, not the best wording in my statements I know I hope you can understand