AusLee
Electrical
- Sep 22, 2004
- 259
Hi,
A street lighting circuit, with single phase fittings but connected to a 3 phase supply. Each next fitting is on a different phase, overall reasonably balancing the neutral.
The question is: the code allows 5% voltage drop. Now i'm looking at this as follows: the fitting is single phase, rated 230V, so it can tolerate as per its appliance standard a maximum Vd of 5%, that it 5% off 230V = 11.5V or 218.5V minimum at the last fitting.
Someone is saying that because it's a 3 phase circuit, you're allowed 5% off the 400V (three phase for 230), which means the margin is 0.05 * 400 = 20V. I'm thinking this is an abstract number that does not correspond to anything. If it was a 3 phase load then yes it would be accepting a 380V minimum, but all loads are single phase.
Can you please advise: 5% is off 230V or 400V on a 3-phase circuit of single phase devices?
Cheers!
A street lighting circuit, with single phase fittings but connected to a 3 phase supply. Each next fitting is on a different phase, overall reasonably balancing the neutral.
The question is: the code allows 5% voltage drop. Now i'm looking at this as follows: the fitting is single phase, rated 230V, so it can tolerate as per its appliance standard a maximum Vd of 5%, that it 5% off 230V = 11.5V or 218.5V minimum at the last fitting.
Someone is saying that because it's a 3 phase circuit, you're allowed 5% off the 400V (three phase for 230), which means the margin is 0.05 * 400 = 20V. I'm thinking this is an abstract number that does not correspond to anything. If it was a 3 phase load then yes it would be accepting a 380V minimum, but all loads are single phase.
Can you please advise: 5% is off 230V or 400V on a 3-phase circuit of single phase devices?
Cheers!