500 Hz power transformer noise
hhhansen
61
I have performed a number of noise recordings for a 20 MVA 132/50 kV transformer, ONAN.
As expected there is a 100 Hz component and multipla of this 100+n*100 Hz due to magnetostriction etc.
However I detect a very huge 500 Hz noise component in the noise frequency spectrum. I have cross validated measurements with a consulting engineering company and they made the same conclusion regarding a dominant 500 Hz component.
This must be a symptom of something particular problem for the transformer but what??.
I have made a lot of noise recordings on similar transformers and I have never experienced a very dominant 500 Hz sound like this
Hans-Henrik
Are you sure whether this 500 Hz component is from the core? Other vibrating fixtures on transformers also may give out noise, sometimes with a resonance frequency.
First, what is the system frequency where you are located?
The system frequency is 50 Hz.
The 500 Hz noise is coming from internal of the transformer from my opinion. There are no loose parts exterior causing resonance
I would have also said that it was the fault of loose metal components/accessories on the tank, as suggested by prc; otherwise, the only thing that comes to mind is the presence of a very strong 5th harmonic in the load current.
The noise records have been made for an unloaded transformer.
If it is a new one or recently serviced, core clamp structure became loose and is resonating at some weird freq? Or worse, some tools were left and are dancing around due to magnetostriction ?
Muthu
If it is a core clamping issue or a windings clamping issue, do you know if the clamping system on the windings has some sort of a hydraulic compression system? The coil stack column may have shrunk due to degradation and now is loose. Helpful if we know the age of the transformer and whether it is a candidate for removal.