There are no set-screw type mechanical lugs I know of that are rated for DLO. I've heard there are / was a saddle clamp type of lug that was listed, but it may have been pulled from the market. You should therefore ONLY use compression lugs and they must be specifically listed for DLO and used with a die that impresses a code saying it was the right kind of die. So you cannot use DLO in applications where the terminations can only be done with mechanical lugs, such as circuit breakers or contactors that have built-in mechanical lugs that cannot be removed for compression lug terminations.
Sizes under 1/0 are not CT (cable tray) rated.
Although it's technically OK to pull properly listed DLO in conduit, there is no amount of lube in the world that makes that easy. The jacket sticks to everything and you can't get the lube to follow it for very long. I've had to do it, I don't want to ever again.