Electrical
- Jun 26, 2007
- 138
I have read thread faq237-1224 as a starter
someone has authorised up grading a vent fan motor on a ship. existing motor was 3kw 60Hz 440V
I was called today as they are setting to work and existing overload is tripping after 2 mins (thankfully).
The new motor selected was 4kW 50Hz 400V. Deliberated selected I am told so as to achieve greater air flow to ships internal compartments, but without a radical redesign of the exhaust air system. The nominal current draw is 10 amps.
The electricians advised that the existing 6.5A overload was tripping when set to work. This tripped after 2 mins. In this time current draw was measured and it was 12.5amps.
The question I have is I am safe to upgrade the overload given that motor will run 12.5A (whereas the nominal is 10A, so 25% over). I guess this translates into 56% additional heat loss using I squared relationship. Is the fact that the motor is running 20% faster going to aid cooling.
My initial thoughts are no they should have picked a bigger motor. There should have been a thermistor connected as part of original design but this was never wired up, I'd feel more comfortable in increasing overload size and monitoring the motor over a couple of days if this was fitted.
Is it a case that motor life will be severely shortened? We basically need 1-2years before the ship is decommissioned. Or is it an outright fire hazard in which case reject the move to increase the overload and have a rethink on options. If so what could be done, a VFD?
appreciate your help.
someone has authorised up grading a vent fan motor on a ship. existing motor was 3kw 60Hz 440V
I was called today as they are setting to work and existing overload is tripping after 2 mins (thankfully).
The new motor selected was 4kW 50Hz 400V. Deliberated selected I am told so as to achieve greater air flow to ships internal compartments, but without a radical redesign of the exhaust air system. The nominal current draw is 10 amps.
The electricians advised that the existing 6.5A overload was tripping when set to work. This tripped after 2 mins. In this time current draw was measured and it was 12.5amps.
The question I have is I am safe to upgrade the overload given that motor will run 12.5A (whereas the nominal is 10A, so 25% over). I guess this translates into 56% additional heat loss using I squared relationship. Is the fact that the motor is running 20% faster going to aid cooling.
My initial thoughts are no they should have picked a bigger motor. There should have been a thermistor connected as part of original design but this was never wired up, I'd feel more comfortable in increasing overload size and monitoring the motor over a couple of days if this was fitted.
Is it a case that motor life will be severely shortened? We basically need 1-2years before the ship is decommissioned. Or is it an outright fire hazard in which case reject the move to increase the overload and have a rethink on options. If so what could be done, a VFD?
appreciate your help.