577 volts to 480volts?

Status
Not open for further replies.

harveytonely

Electrical
Jan 29, 2009
2
We are running 480 volt 3 pahse at our facility. We found a deal on a piece of equitment we need,but the motor is wound for 577 volts. Would it be alright to run this motor at 480 volts and expecting slightly more amp draw?
 
Replies continue below

Recommended for you

Probably not. That's a big difference in voltage.

If you are getting such a good deal, you'll be able to buy an autotransformer with all that extra money and boost the voltage up to what it should be.



 
Yea ,I could do that but I have a very small inside cabinet that is aleady loaded with no room. Besides that everything else is 480 volts so it might confuse someone after me, especially if a nameplate got to missing. If it would be a big problem I would just have the motor rewound. Thanks for the reply.
 
The autotransformer is a good solution - much less costly than trying to rewind the motor. But whatever you think.

Pretty sure you won't be happy running the 577 V motor at 480 V.
 
Post the motor rated Full Load Amps at 577 Volts and we can show you a sample transformer size. The transformers may be much smaller than you suspect. I have encountered this issue a lot. I typically mount the transformers close to the motor. Is this a 60 Hz motor?

Bill
--------------------
"Why not the best?"
Jimmy Carter
 


Every time you ask something about motors, you need to write all the details from the nameplate..
Zlatkodo
 
Sample calculation;
Motor current = 5 Amps
Boost needed = 120 volts
KVA = 5A x 120V / 1000 = 0.6 KVA
For this example motor you would need 2 boost rated 480:120 Volt transformers connected in open delta auto-transformer boost configuration. Dry type transformers may be mounted outside a panel or control enclosure. I have mounted them on the floor beside the motor at times.


Bill
--------------------
"Why not the best?"
Jimmy Carter
 