RRaghunath
Electrical
- Aug 19, 2002
- 1,729
We are looking for indoor metal clad switchgear for a power plant. The requirement is the incomer shall have 3000A in-panel rating at a reference ambient of 50degC.
I know VCBs and SF6 CBs are available with 3150A rating but at 40degC (IEC reference temperature).
One estimate is the 3150A breaker at 50degC ambient and with IEC temperature rises (with silver plated joints) can only have 2400A in-panel rating.
I am aware we can have the required rating in GIS range, but it is expensive and do not want to consider at this stage.
Appreciate any help. Thanks in anticipation.
I know VCBs and SF6 CBs are available with 3150A rating but at 40degC (IEC reference temperature).
One estimate is the 3150A breaker at 50degC ambient and with IEC temperature rises (with silver plated joints) can only have 2400A in-panel rating.
I am aware we can have the required rating in GIS range, but it is expensive and do not want to consider at this stage.
Appreciate any help. Thanks in anticipation.