Hi all,
because space constraints we are considering to drive six 4 kW, 400 V identical 10-pole, PM AC, sensorless motors with only one VFD. The applied torque on each of the six motors is NOT the same and varies with time.
I understand the logic that the VFD will fail to determine the rotor(s) position with the usual high frequency current injection, because the initial rotor position of the six motors won't be the same at start-up... but what if we use the following starting strategy:
[ol 1]
[li]remove all load from the six motors (this we can do very easily)[/li]
[li]start feeding a very low frequency (say 1 Hz) for a sufficiently long period (say 10 s). This should allow for the rotors to start moving and to the six of them to achieve the same phasing.[/li]
[li]then gently ramp the motors up to speed, to avoid inertia to overcome the ramping speed.[/li]
[li]then apply load.[/li]
[/ol]
Is all this just horribly wrong and plain madness?
Thanks!
because space constraints we are considering to drive six 4 kW, 400 V identical 10-pole, PM AC, sensorless motors with only one VFD. The applied torque on each of the six motors is NOT the same and varies with time.
I understand the logic that the VFD will fail to determine the rotor(s) position with the usual high frequency current injection, because the initial rotor position of the six motors won't be the same at start-up... but what if we use the following starting strategy:
[ol 1]
[li]remove all load from the six motors (this we can do very easily)[/li]
[li]start feeding a very low frequency (say 1 Hz) for a sufficiently long period (say 10 s). This should allow for the rotors to start moving and to the six of them to achieve the same phasing.[/li]
[li]then gently ramp the motors up to speed, to avoid inertia to overcome the ramping speed.[/li]
[li]then apply load.[/li]
[/ol]
Is all this just horribly wrong and plain madness?
Thanks!