Are there any code/safety restrictions for mounting a new 480vac/600A Distribution panel next to a doorway? Within a 2 feet?
 
Replies continue below

Recommended for you

Not really. You need to maintain clear passage in and out of the doorway. Article 110 covers working space requirements in excruciating detail.
 
You might check the local building codes for any required architectural clearances.
 