designrider
Structural
- Oct 25, 2007
- 50
I recently designed an aluminum structural frame for a 5’x160’ long pedestrian bridge using various sizes of extruded 6061-T6 aluminum sections. Most connections were aluminum welded. I specified 5356 filler wire and mainly 1/8” fillet welds (which fabrication upsized to 3/16-1/4” nearly everywhere). The fabrication shop performed a very sub-par job and failed inspection because of cracks in dozens of welds. The inspector called us to specify a repair plan; he thought most of the cracks were the result of inadequate base metal preparation and pre-heating. Does anyone have suggestions on the best repair option(s).
AWS D1.2 (Struct Weld Code-Aluminum) section 4.20 shows that the welds can either be repaired or removed and replaced. Removing the entire weld would be a cumbersome project for the amount of welds that are cracked. However, removal of the “unacceptable portion” is likely what needs to take place. Would specifying that the cracked weld portion be removed plus a distance 1/8" past end of crack, then replacing weld be adequate? I have also heard of stop-drilled holes to arrest the crack, but the size of hole recommended (3/4” or greater) seems excessive and a threat to the structural sections themselves, and likely more applicable to butt welds rather than fillet welds.
Where redundancy exists in my design, can I permit that some welds remain cracked, and essentially assume the cracked weld has become nothing more than ‘debris’ on the frame? Or does a cracked weld introduce problems regardless of its structural “need” (ie. a cracked weld is worse than no weld at all).
Finally, where a weld group exists, can a longitudinal crack in one weld propagate into an overlapping weld that runs perpendicular?
Thanks!
AWS D1.2 (Struct Weld Code-Aluminum) section 4.20 shows that the welds can either be repaired or removed and replaced. Removing the entire weld would be a cumbersome project for the amount of welds that are cracked. However, removal of the “unacceptable portion” is likely what needs to take place. Would specifying that the cracked weld portion be removed plus a distance 1/8" past end of crack, then replacing weld be adequate? I have also heard of stop-drilled holes to arrest the crack, but the size of hole recommended (3/4” or greater) seems excessive and a threat to the structural sections themselves, and likely more applicable to butt welds rather than fillet welds.
Where redundancy exists in my design, can I permit that some welds remain cracked, and essentially assume the cracked weld has become nothing more than ‘debris’ on the frame? Or does a cracked weld introduce problems regardless of its structural “need” (ie. a cracked weld is worse than no weld at all).
Finally, where a weld group exists, can a longitudinal crack in one weld propagate into an overlapping weld that runs perpendicular?
Thanks!