60Hz generator to 50Hz

Status
Not open for further replies.

Emadshaaban1987

Electrical
Apr 30, 2020
58
hello folks,
in general, How can i change the frequency of the output of 10KVA generators?
 
Replies continue below

Recommended for you

And change the UFRO jumper from 60Hz to 50 Hz.
Adjust the voltage and the stability of the AVR.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
LittleInch said:
Buy a convertor?
That will work, but it is a lot of money to spend when two adjustments and moving a jumper will accomplish the same result.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Maybe he can't change the speed of the prime mover? It's just an option.

No details so who knows?

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 
Dear Mr. LittleInch
" Maybe he can't change the speed of the prime mover? It's just an option." I agreed.
It's just "another" option. Throw away the existing set and buy a " new " set, with the correct frequency and voltage. Simple. Any one disagreed (sarcastic)?

Che Kuan Yau (Singapore)
 
Awful waste of a perfectly good 60 Hz generator to just throw it away; maybe sell it used and get some cash for it?

What davidbeach and Bill said; be aware however that the capacity of the unit will be 5/6 of its 60 Hz rating.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]
 
You haven't told us what voltage you want at 50 Hz.
The maximum line to neutral voltage setting of a three phase, 60 Hz. generator is often 138 Volts per winding.
For 50 Hz that becomes 115 Volts per winding.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 