ThePunisher
Electrical
- Nov 7, 2009
- 384
HI all,
We have specified ratings as per ANSI at 65 Deg C Rise and our client asked us to specify dual 55/65 Deg C rises to take advantage of the extra capacity.
For example, taking a 15/20 MVA ONAN/ONAF transformer with a 65C rise and changing it to a 55/65 would change the rating to a 15/20/22.4 MVA. This is still ONAN/ONAF with dual ONAF capability right? OR is it ONAN/ONAF1/ONAF2?
I looked into ANSI C57 but am not able to find a direct rating comparison for both 65 and 55/65 rises and is giving me some confusion.
I have two other transformers with standard 65 Deg C rise rating: 25/33.3/41.6 MVA and 1/1.33 MVA. if I will apply the same factor, will the 55/65 deg C counter-part be 25/33.3/37.5 MVA (or 25/37.5 MVA) and 1/1.5 MVA respectively?
Thank you all for your guidance.
We have specified ratings as per ANSI at 65 Deg C Rise and our client asked us to specify dual 55/65 Deg C rises to take advantage of the extra capacity.
For example, taking a 15/20 MVA ONAN/ONAF transformer with a 65C rise and changing it to a 55/65 would change the rating to a 15/20/22.4 MVA. This is still ONAN/ONAF with dual ONAF capability right? OR is it ONAN/ONAF1/ONAF2?
I looked into ANSI C57 but am not able to find a direct rating comparison for both 65 and 55/65 rises and is giving me some confusion.
I have two other transformers with standard 65 Deg C rise rating: 25/33.3/41.6 MVA and 1/1.33 MVA. if I will apply the same factor, will the 55/65 deg C counter-part be 25/33.3/37.5 MVA (or 25/37.5 MVA) and 1/1.5 MVA respectively?
Thank you all for your guidance.