If both 67N (directional ground fault) and 51N (non-directional ground fault) are available in a relay, which one would you prefer to use?
My colleague suggests that 67N is a better choice because it incorporates zero-sequence voltage, while 51N does not. As a result, 67N is less likely to cause nuisance trips and operates only for actual faults. What are your thoughts on this? Also, how do you typically test 67N (directional earth fault) during commissioning? Is it necessary to earth one phase of the system for testing, especially in a high-impedance grounded system?
My colleague suggests that 67N is a better choice because it incorporates zero-sequence voltage, while 51N does not. As a result, 67N is less likely to cause nuisance trips and operates only for actual faults. What are your thoughts on this? Also, how do you typically test 67N (directional earth fault) during commissioning? Is it necessary to earth one phase of the system for testing, especially in a high-impedance grounded system?