690V 50Hz

Status
Not open for further replies.

JJAC

Electrical
Aug 29, 2005
1
I am looking at a project in Mongolia where the voltages appear to go from 230V 1 ph, 380 3 ph then to 690V 3 ph with distribution at 10.5kV Of interest 690 V for >200 kW.
690 V appears to be 400xroot3 indicating a 400V motor winding in star rather than delta.
Is 690 V a common Non US voltage? IEC perhaps?
International drive manufacturers appear to list it as do foreign motor manufacturers.
Any comments
 
Replies continue below

Recommended for you

Common in some applications, such as undergound mining where distribution distances can be great. Higher volage = lower current = more distance out of a given wire size.

"Our virtues and our failings are inseparable, like force and matter. When they separate, man is no more." Nikola Tesla

Make the best use of Eng-Tips.com
Read the Site Policies at faq731-376

 
Many industrial installations in Europe have 690 V isolated (IT) with no neutral. It is the standard used for most new paper mills where many drives are in the 1+ MW range.

The former 500 V system is not used much any more. The 690 V systems have been around for more then ten years and seem to replace the earlier 500 V IT systems.

Gunnar Englund
 