69kV XLPE Routing in Cable Tray 2

Status
Not open for further replies.

rockman7892

Electrical
Apr 7, 2008
1,159
Are there any issues or limitations with routing 69kV XLPE Power Cable in cable tray in an industrial environment? What about above ground conduit?

I usually see such installations as being installed underground but this is located in an existing industrial facility where UG routing is not really practical. There are existing pipe & cable racks which could potentially be used for supporting cable tray or conduit.

Thanks
 
Replies continue below

Recommended for you

A cable tray is a suitable means to run a 69 kV power cable. The cable should be fastened to the tray and EGC should be considered with the appropriate size.

The conduit can also be used. Careful should be exercised with a single-core cable running in steel conduit to avoid heating and hysteresis losses

See the illustration below that may have some answers to your enquire.

Power_Cable_69_kV_in_Cable_Tray_kjo9wg.jpg
 