Hi,
I have a standy generator set rated 950kVA 415V 50Hz. Recently we tried to commission the genset with the biggest load being 160kW (first block). However, the load cannot be transfered to the genset. The load is using Direct-on-line (DOL) starter. The allowable voltage dip during starting is 15%. We believe the load(with DOL starting) is too big for the genset to pick up. Is it really? The load was supposed to be 132kW during design and procurement stage. Questions:-
a) Is there anything wecan modify ( on the genset) to make the genset pick up the load?
b) We are looking at other options of motor starting to reduce the starting current ( say, 300%)so that the genset can pick it up. What would be the most either convenient, cost effective and practical solutions
c) If we choose a starting method to reduce the starting current what are the things that we need to consider
Thanks in advance for your prompt reply.
rgds,
Zak
I have a standy generator set rated 950kVA 415V 50Hz. Recently we tried to commission the genset with the biggest load being 160kW (first block). However, the load cannot be transfered to the genset. The load is using Direct-on-line (DOL) starter. The allowable voltage dip during starting is 15%. We believe the load(with DOL starting) is too big for the genset to pick up. Is it really? The load was supposed to be 132kW during design and procurement stage. Questions:-
a) Is there anything wecan modify ( on the genset) to make the genset pick up the load?
b) We are looking at other options of motor starting to reduce the starting current ( say, 300%)so that the genset can pick it up. What would be the most either convenient, cost effective and practical solutions
c) If we choose a starting method to reduce the starting current what are the things that we need to consider
Thanks in advance for your prompt reply.
rgds,
Zak