RRaghunath
Electrical
- Aug 19, 2002
- 1,729
A 11kV, 5000kW motor is provided with Differential protection. This motor has PF correction capacitors of 1.9MVAR coming within the zone of differential protection (due to the specific location of CTs).
This will mean that the PFCC current is not accounted in the differential scheme and thus requires the differential protection to be set less sensitive so as not to have tripping on the PFCC current that is going to appear as spill in the relay.
Any experiences / suggestions.
Thanks in anticipation.
This will mean that the PFCC current is not accounted in the differential scheme and thus requires the differential protection to be set less sensitive so as not to have tripping on the PFCC current that is going to appear as spill in the relay.
Any experiences / suggestions.
Thanks in anticipation.