Hello
I will talk about Eurocode (EC) provisions in relation to the topic, but most likely other codes have similar provisions too.
Acc. to EC1-1-2:
1.5.1.12
member analysis (for fire)
thermal and mechanical analysis of a structural member exposed to fire in which the member is assumed as isolated, with appropriate support and boundary conditions. Indirect fire actions are not considered, except those resulting from thermal gradients
1.5.1.7
indirect fire actions
internal forces and moments caused by thermal expansion
Basically the member analysis allows to extract any kind member from a system and design it as isolated regardless of any other actions developed in the system. It seems ok if stability of the system assured by some other measures.
Imagine a 2-span single storey frame with columns rigidly fixed at base. No bracings at all i.e stability of the hall rely solely on the cantilever action of the columns. Girders are simply supported on top of the columns. Under fire the girders are going to expand, push top of the edge columns outward and definitely produce additional bending moments in the base of the columns. If the base of the columns become a plastic hinge, there are risk of the columns to fall outward. But according to the "member analysis" we may disregard all of that. This doesn't seem right for me at all. I have tried to find any design examples in literature for the case or something similar without luck.
I have a dispute with a colleague about the matter. He doesn't want to bother of any interpretation of the code provisions. So he isolated the columns applied all external actions (wind, self-weight, dead loads) required for the fire design situation, omitted the indirect fire actions and figured out critical temperature for the columns. Fire painted only the columns for the critical temperature. Asserts this is enough. But the expansion of the girders is not going to be affected by the painting. So the risk is still there. It seems to me wrong to the core.
Are you agree to use the member analysis provisions for the case?
Does anyone have a good reference publication discussing stability of cantilever steel columns in fire? I know P313 "Single storey steel framed buildings in fire boundary conditions", but it can not be directly applied to the case.
Regards
I will talk about Eurocode (EC) provisions in relation to the topic, but most likely other codes have similar provisions too.
Acc. to EC1-1-2:
1.5.1.12
member analysis (for fire)
thermal and mechanical analysis of a structural member exposed to fire in which the member is assumed as isolated, with appropriate support and boundary conditions. Indirect fire actions are not considered, except those resulting from thermal gradients
1.5.1.7
indirect fire actions
internal forces and moments caused by thermal expansion
Basically the member analysis allows to extract any kind member from a system and design it as isolated regardless of any other actions developed in the system. It seems ok if stability of the system assured by some other measures.
Imagine a 2-span single storey frame with columns rigidly fixed at base. No bracings at all i.e stability of the hall rely solely on the cantilever action of the columns. Girders are simply supported on top of the columns. Under fire the girders are going to expand, push top of the edge columns outward and definitely produce additional bending moments in the base of the columns. If the base of the columns become a plastic hinge, there are risk of the columns to fall outward. But according to the "member analysis" we may disregard all of that. This doesn't seem right for me at all. I have tried to find any design examples in literature for the case or something similar without luck.
I have a dispute with a colleague about the matter. He doesn't want to bother of any interpretation of the code provisions. So he isolated the columns applied all external actions (wind, self-weight, dead loads) required for the fire design situation, omitted the indirect fire actions and figured out critical temperature for the columns. Fire painted only the columns for the critical temperature. Asserts this is enough. But the expansion of the girders is not going to be affected by the painting. So the risk is still there. It seems to me wrong to the core.
Are you agree to use the member analysis provisions for the case?
Does anyone have a good reference publication discussing stability of cantilever steel columns in fire? I know P313 "Single storey steel framed buildings in fire boundary conditions", but it can not be directly applied to the case.