thewolfofconcrete
Structural
- Sep 12, 2022
- 4
I've been a lurker for years, but the issue at hand has me so turned around I finally decided to make an account and post the question. I'm hoping that the intelligence of the masses can help me out.
Here is the issue: I work for a precast designer and supplier that was asked by an EOR what the "tension" capacity was between our precast plank and a poured and bonded topping, specifically for ICC 500 compliant storm shelters. The engineer (my colleague) who was asked this question didn't have an answer prepared at the time, so the EOR took the position that interface ties (repurposed lifting loops, in our case) are required on a 4' x 4' grid at the precast roof to provide tensile bond between the plank and the topping. Their position is that if a tornado hits the storm shelter, the "uplift forces" will "suck" the topping off the precast plank. There are clear and established standards for plain interface shear capacity, but direct tension on this interface is distinctly different in our eyes.
I wrote a letter attached to a calculation packet that used a first principle physics argument to contend that no interface ties were required, because no such force exists to pull a bonded topping off of precast plank. By nature, gasses and fluids cannot pull on an object. Pressure differentials can push on objects, but they cannot pull on them. In our case, the pressure differential exists between the inside of the building and the outside so it pushes on the entirety of the precast roof assembly. Intuitively, this force could never cause the topping to "fly away". If you have a sub sandwich, and you push on the bottom bun, the top bun will not move, the whole sandwich will.
The EOR rejected this argument and maintained their position that suction does exist and interface ties are required if we cannot provide a calculation or reference for the tensile capacity of concrete topping on precast plank.
Complicating the issue is that ASCE 7 repeatedly uses nomenclature, figures, and sign conventions that suggest or imply "suction" forces on wall and roof assemblies. Reference 7-16 sec. 26.4.1, fig. 27.3-1, fig. 30.3-1, etc...
I welcome any and all comments on this issue. Thanks in advance, guys.
Here is the issue: I work for a precast designer and supplier that was asked by an EOR what the "tension" capacity was between our precast plank and a poured and bonded topping, specifically for ICC 500 compliant storm shelters. The engineer (my colleague) who was asked this question didn't have an answer prepared at the time, so the EOR took the position that interface ties (repurposed lifting loops, in our case) are required on a 4' x 4' grid at the precast roof to provide tensile bond between the plank and the topping. Their position is that if a tornado hits the storm shelter, the "uplift forces" will "suck" the topping off the precast plank. There are clear and established standards for plain interface shear capacity, but direct tension on this interface is distinctly different in our eyes.
I wrote a letter attached to a calculation packet that used a first principle physics argument to contend that no interface ties were required, because no such force exists to pull a bonded topping off of precast plank. By nature, gasses and fluids cannot pull on an object. Pressure differentials can push on objects, but they cannot pull on them. In our case, the pressure differential exists between the inside of the building and the outside so it pushes on the entirety of the precast roof assembly. Intuitively, this force could never cause the topping to "fly away". If you have a sub sandwich, and you push on the bottom bun, the top bun will not move, the whole sandwich will.
The EOR rejected this argument and maintained their position that suction does exist and interface ties are required if we cannot provide a calculation or reference for the tensile capacity of concrete topping on precast plank.
Complicating the issue is that ASCE 7 repeatedly uses nomenclature, figures, and sign conventions that suggest or imply "suction" forces on wall and roof assemblies. Reference 7-16 sec. 26.4.1, fig. 27.3-1, fig. 30.3-1, etc...
I welcome any and all comments on this issue. Thanks in advance, guys.