As a sequel to a request that I placed on Eng-Tips (thread238-408206) some 10 months ago; I offer the follow-up:
Original Post
Howdy,
Does anyone have any experience with limiting transformer inrush current. I have several (separate) locations that will experience excessive voltage drop on the incoming Utility feeder. Feeder is 25kV and transformer sizes range from 3MVA up to 12.5MVA. I was thinking of simply using a 25kV reactor, c/w bypass contactor to limit the current to (say) < 2 X IFL. Normal inrush for these transformers in 4.5 to 5.5 x IFL @ 1.0puV.
Voltage-drop w/o these reactors will vary between 25% to over 50%. This level of voltage-drop will not be appreciated by other users on the 25kV feeders.
Thanx
Follow-Up
To date we have had 5 Sites that required a remedy to the issue stated above. Target voltage-drop to be < 6% (per the Utility's request).
Two are now fully commissioned, two will be commissioned in the next few weeks, and one is still in the design stage.
At all Sites the solution was to install one (1) 25kV current-limiting reactor c/w bypass-contactor per Site.
We considered other technologies, such as Point-On-Wave, but decided that the reactor-bypass contactor was the best option with the lowest TIC.
The current-voltage graphs attached to this report were for a site with two transformers rated:
- 5MVA 25kV-4160V
- 2MVA 4160V-600V
Without the reactor, a voltage-drop (at the PoCC with the Utility) was calculated to be > 40%.
With the reactor in place, the recorded voltage-drop was limited to < 4%.
I will post one more time when the 12.5MVA Site has been commissioned.
Regards
GG
ps If you require any further information, the writer may be contacted at randy@kyebaysystems.com
"I have not failed. I've just found 10,000 ways that won't work." Thomas Alva Edison (1847-1931)
Original Post
Howdy,
Does anyone have any experience with limiting transformer inrush current. I have several (separate) locations that will experience excessive voltage drop on the incoming Utility feeder. Feeder is 25kV and transformer sizes range from 3MVA up to 12.5MVA. I was thinking of simply using a 25kV reactor, c/w bypass contactor to limit the current to (say) < 2 X IFL. Normal inrush for these transformers in 4.5 to 5.5 x IFL @ 1.0puV.
Voltage-drop w/o these reactors will vary between 25% to over 50%. This level of voltage-drop will not be appreciated by other users on the 25kV feeders.
Thanx
Follow-Up
To date we have had 5 Sites that required a remedy to the issue stated above. Target voltage-drop to be < 6% (per the Utility's request).
Two are now fully commissioned, two will be commissioned in the next few weeks, and one is still in the design stage.
At all Sites the solution was to install one (1) 25kV current-limiting reactor c/w bypass-contactor per Site.
We considered other technologies, such as Point-On-Wave, but decided that the reactor-bypass contactor was the best option with the lowest TIC.
The current-voltage graphs attached to this report were for a site with two transformers rated:
- 5MVA 25kV-4160V
- 2MVA 4160V-600V
Without the reactor, a voltage-drop (at the PoCC with the Utility) was calculated to be > 40%.
With the reactor in place, the recorded voltage-drop was limited to < 4%.
I will post one more time when the 12.5MVA Site has been commissioned.
Regards
GG