Section 3.28 of the AASHTO Standard Specifications defines the methods for calculating the live load distribution factor for a prestressed concrete spread box beam superstructure.
Equation 3-33 of this section consists of a number of variables, two of which have defined upper and lower bounds.
The variable S is defined as the beam spacing, for which only the following values (in feet) are applicable: 6.57<=S<=11.00.
The variable W is defined as the curb-to-curb width of the roadway, for which only the following values (in feet) are applicable: 32<=W<=66.
Unfortunately, the code does not specify how to calculate your distribution factor should either or both of these variables fall outside these limits.
One option could be to use the method described in Table 3.23.1 for prestressed concrete girders (S/5.5), since they are in fact prestressed concrete girders, just with a box shape. However, because of the wide widths of the boxes, I can see where this might not be applicable.
Alternatively, it seems that the most conservative approach would be to calculate the distribution factor assuming the deck slab acts as a simple beam spanning between the box beams. This method (footnote f in Table 3.23.1) is defined for most longitudinal beam bridges with widely spaced beams.
My firm is currently working on the design of a small bridge with curb-to-curb widths and beam spacings outside of the lower bounds of both variables in question. A comparison of the S/5.5 method to the simple span lever method for this particular bridge results in a 23% higher distribution factor for the lever method.
Incidentally, we are using CONSPAN by LEAP Software to assist with the design, and the program (confirmed by LEAP support engineers) is using the lever method.
Have you run into this situation before? Any comments on this?
Equation 3-33 of this section consists of a number of variables, two of which have defined upper and lower bounds.
The variable S is defined as the beam spacing, for which only the following values (in feet) are applicable: 6.57<=S<=11.00.
The variable W is defined as the curb-to-curb width of the roadway, for which only the following values (in feet) are applicable: 32<=W<=66.
Unfortunately, the code does not specify how to calculate your distribution factor should either or both of these variables fall outside these limits.
One option could be to use the method described in Table 3.23.1 for prestressed concrete girders (S/5.5), since they are in fact prestressed concrete girders, just with a box shape. However, because of the wide widths of the boxes, I can see where this might not be applicable.
Alternatively, it seems that the most conservative approach would be to calculate the distribution factor assuming the deck slab acts as a simple beam spanning between the box beams. This method (footnote f in Table 3.23.1) is defined for most longitudinal beam bridges with widely spaced beams.
My firm is currently working on the design of a small bridge with curb-to-curb widths and beam spacings outside of the lower bounds of both variables in question. A comparison of the S/5.5 method to the simple span lever method for this particular bridge results in a 23% higher distribution factor for the lever method.
Incidentally, we are using CONSPAN by LEAP Software to assist with the design, and the program (confirmed by LEAP support engineers) is using the lever method.
Have you run into this situation before? Any comments on this?