Most likely because two distinct alarm signals will be initiated before the CO2 system discharges:
1) Activation of the occupant notification devices upon operation of the initiating device
2) A separate and distinct pre-discharge alarm before CO2 is released
I would say it's likely because CO2 is deadly, and you don't want someone going into or staying in an area where a CO2 system has activated to hold the abort station.