AC Condenser Pad Design Tips

Status
Not open for further replies.

Acemas99

Automotive
Mar 7, 2012
1
Hello All,

I have used Eng-Tips throughout my college career, but this is my first time posting a thread.

I am designing a concrete AC condenser pad. The pad will likely be 42" x 42" x 4" and will contain a foam core to reduce the overall weight. The current target weight is 265 lbs, which is driven by the Florida Hurricane requirements.

I am wondering what basic design features I can incorporate to reduce the risk of cracking. I'd like to keep the cost as low as possible, so I am trying to avoid re-bar. I'm looking more for tips on the shape / geometry of the foam, wall thicknesses of the concrete, etc.


 
Replies continue below

Recommended for you

Agree with bimr and Mike...if you must have a concrete slab, look in the Florida Building Code....it gives a prescriptive method.

Don't worry about cracking....your slab is small, so shrinkage cracks, assuming a thickness of 4 inches, shouldn't be an issue.

I would thicken the edges to reduce scour/undermining potential.
 