AC power cord length restrictions 1

Status
Not open for further replies.

SysEng38

Electrical
Feb 13, 2003
2
I am trying to provide ac power to a chassis unit that is located 800' away. In this unit, I have four linearly regulated DC power supplies. I am considering in using an AC power cord to supply power to my power supplies. What is the length restriction for using ac power cords in the outdoors? Do I need driver amplifiers for my application?
 
Replies continue below

Recommended for you

I would reconsider your position on the use of a cord. I don't recall any length restriction, however, being that it's 800' long(?!), I would definitely recommend a permanent solution like pipe and wire to a location nearby(within say 10'), and then you can run a cord if so desired. If you're in the US, you should check article 400 of the NEC, because it gives specific uses of cords in that section(400.7 & 400.8).

Mike
 
SysEng38,

1) What is the total power, in Watts, or VA, that you are tryng to supply, 800' away?

3) What is the required voltage?

3) Have you thought about splitting the 4 units up, and suppling them with a 3-ph/4-wire circuit?
 
T100,
For a related topic, see thread 278-44947,

"3-Phase to Single-Phase Current Relationships"
 
mpparent:

I am working in the US. My application is to remotely turn on power supplies at a distance of 800'. The supplies are located near an AC outlet, however, it is cumbersome to have to plug and un-plug an ac power cord. The ac outlet is located on a pier and I am on a cliff that is located 800' away.

Shortstub:

Here are my answers:
1) 70 watts
2) 120 Vac at 800'
3) No, I have not--it seems involved. The supplies have to be co-located and housed in a weather-tight enclosure. My application is to remotely turn on the supplies. I would like to have a 'toggle switch' that is 800' away. I am trying to avoid making many trips to this enclosure and turn on the supplies.
 
SysEng38, are you asking if you need driver amplifiers for your AC supply? If you don't usually do this kind of work (Power) refer to a qualified person. An 800' run of extension cords is not a practical wiring method.
First, the load must be determined, and the voltage drop for this load must be calculated for this distance at the load's voltage (in a professionally installed wiring method). If the voltage drop is excessive (and it almost certainly will be), you may need oversized conductors or the use of a higher voltage for the 800', and then transformation down to your load voltage.
 
Suggestion: The permanent or temporary nature of this installation needs to be determined. It makes a difference from safety standpoint. Temporary installations accepts cords. The proper size of the cord is needed, e.g. #12AWG, however, this would assume that there is a regular load with acceptable voltage tolerance plus minus 5% or so and no motor loads with high inrush currents.
 
If I understand your situation correctly, there is AC power at the load, but it is inconvenient to get to the load to turn it on and off. I would consider a radio controlled switch for the load. If there is a phone at the load, you could get an X10 switch that can be controlled by telephone (see You might find something at Radio Shack that could be used.

Running an 800 ft cord, especially when part of it is on a pier, would be out of the question. It would be dangerous and there would probably be too much voltage drop.
 
You might also consider a power-line modem. At the refinery in Anacortes, WA there are several which control pumps, down on the pier, at a distance of some 1500 feet.
 
Conductor length is limited by voltage drop. Voltage drop calcs depend on conductor size, type, and arrangement, conduit type, and load current. The calcs are not rocket science, but I agree that you should get an engineer or at least a sharp designer or electrician to work with you on this.

Another way to achieve hard-wired control would be to use a control relay or contactor to switch the loads. That way only a very small control-power current would have to traverse the 800-foot wiring run and voltage drop would become much less of an issue.

I agree that radio or phone might be more convenient and possibly cheaper.

 

Something like a 24VDC "ice cube" relay [P&B KRP?] with small DC power supply may do the job. Consider 2-pair 24AWG telecomm cable: One pair to switch the realy coil and one to send back a contact closure.
 