ACCU Starting

Status
Not open for further replies.

alanElec

Electrical
Feb 14, 2013
78
Anybody here have any idea about working of Air cooled condensing units? They have more than one compressor..I want to know wheather all these compressors turn on simultaneously or in steps..? I wanted to know the starting current..
 
Replies continue below

Recommended for you

They will turn on in steps. Use 6 times running current and 3 or four times rated kW due to the very low power factor when starting.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Yes they will..For example an ACCU has two circuits of 2 compressors each.Each Compressor having a KW of 100.So max starting current can be 3*(100+100)? and not 3*(100+100+100+100)..
 