edison123
Electrical
- Oct 23, 2002
- 4,460
I did a VFD motor testing at the VFD supplier's factory. We used a Fluke 434 PQ analyzer to measure drive output voltage, current, KW, frequency etc.
PQ analyzer showed output was 400 V while the drive's own panel output meter showed only 370 V. Fluke DMM also showed 400 V output.
The KW, Amps, frequency readings from PQ analyzer were matching with the drive's panel meter.
Why are the PQA and DMM showing higher voltage than the drive's panel meter but the KW, Amp, Hz are matching?
I understand these external DMM / PQA are not designed PWM output of the drive. If so, how to externally measure these output voltages accurately which match the drive's panel meter?
Muthu
PQ analyzer showed output was 400 V while the drive's own panel output meter showed only 370 V. Fluke DMM also showed 400 V output.
The KW, Amps, frequency readings from PQ analyzer were matching with the drive's panel meter.
Why are the PQA and DMM showing higher voltage than the drive's panel meter but the KW, Amp, Hz are matching?
I understand these external DMM / PQA are not designed PWM output of the drive. If so, how to externally measure these output voltages accurately which match the drive's panel meter?
Muthu