I am preparing a master anchor bolt schedule for hold downs in the 2008 simpson strong tie catalog for single family residential. The design software provided by simpson does not do designs for epoxy bolts. Simpson provides an example calculation which follows ACI appen. D for the design of all thread bolts with set XP epoxy. While it is favorable to have any large anchor bolt cast in place at the time of pour, often the lack of skilled labor generates a bolt cast in the incorrect location and thus we must make a repair.
Hold downs with higher allowable loads when factored to generate Nua which must be less that PhiNsa, PhiNcb, and PhiNa, but since these are wood framed homes with 2x6 walls the concrete stem wall is also 6" which limits Camin to 3" which yeilds low bolt capacities none of which satitisfy the D4.1.2. I went back to check old designs for simular cases and per ACI 318 calc those no longer work. Is there truely no approved retro fit for an anchor bolt at a hold down along a stem wall?
Hold downs with higher allowable loads when factored to generate Nua which must be less that PhiNsa, PhiNcb, and PhiNa, but since these are wood framed homes with 2x6 walls the concrete stem wall is also 6" which limits Camin to 3" which yeilds low bolt capacities none of which satitisfy the D4.1.2. I went back to check old designs for simular cases and per ACI 318 calc those no longer work. Is there truely no approved retro fit for an anchor bolt at a hold down along a stem wall?