10k PSI concrete in a 15” x 24” column with 8 # 7 verts.
The mix =
Type I = 495
Slag = 270
Flyash = 135
Natural sand = 992
Stone # 7 (3/8” max) = 1930
33 gal water
153 oz high range water reducer
slump 6 to 8 post SP
air 1 to 3
W/C = .31
One set of 6 test cylinders (6”x12”)
Two 7 day breaks = 6110 and 6190
Two 28 day breaks = 9140 and 9190
Two 56 day breaks = 9860 and 9920
3 Cores tested at 73 days = 9730 and 8180 and 7230
average 8380 psi and 84% of fc
one single core was 72% of fc
Technically the core results failed because the average of the 3 cores was under 85% of fc and one single core was under 75% of fc. Additionally, I think I recall seeing something in the EOR specs about requiring cores to be 90% of fc for fc mixes over 6000psi or 7000psi. I’ll have to look that up.
The point of this post:
ONE core 14” long was drilled from the 15” face. The core was subsequently sawed into THREE pieces to get the ACI-318 required 3 compression tests.
The core nearest the outside of the column was the highest break and the core nearest the inside of the column was the lowest break. Upon coring, I had expected the cores breaks to be within a hundred psi of each other or so, but obviously this did not happen.
ACI-318 5.6.5.2 — If the likelihood of low-strength concrete is confirmed and calculations indicate that load-carrying capacity is significantly reduced, tests of cores drilled from the area in question in accordance with “Method of Obtaining and Testing Drilled Cores and Sawed Beams of Concrete” (ASTM C 42) shall be permitted. In such cases, three cores shall be taken for each strength test that falls below the values given in 5.6.3.3(b).
Two questions:
Does the taking of ONE long core and then sawing it up to get three compression tests satisfy the intent of ACI-318-5.6.5.2.
Also, how does one interpret the core results? The cylinder breaks appear to be dead on the money with those tight numbers but the cores had a difference of more than 2000 psi. Could this be a phenomenon of the vibrating technique used during concrete placement, of a moisture gradient between the exterior and the interior of the column, or of a thermal condition in the interior of the column causing micro cracking at the aggregate?
Techmaximus