Thanks for starting this post Jacst3.
I've been struggling with this also.
I ran some hypothetical cases, and achieved the following results. If anyone can affirm or contest these results, I'd be glad to hear it:
All my cases use a retained liquid of 63 pcf, 21' deep.
All are for a pure cantilever wall holding back liquid.
All are an attempt to determine Mu and the adequacy of steel reinforcing at bottom inside face of wall.
All have 2" clear to face of vertical steel.
All use Fy = 60ksi, F'c = 4.5 ksi
All use a liquid (F) load factor of 1.4
All use Phi = 0.9 for flexure
Calculation is solely for lateral pressure load - ignoring everything else.
By varying the wall thickness and reinforcing, and by going from "normal" to "severe" exposure, the Sd number moves around from 1.13 to 1.49, and Mu changes accordingly.
That is what I have discovered.
Unfactored M at bottom of wall in all cases is 97.2 kip-ft/ft. (.063*21^3/6)
26" wall thickness, "normal" exposure, Verts #8 @ 6"
RESULTS: fs = 34.14, Sd = 1.13 Mu = 153.8 kip-ft/ft and PhiMn = 159.7
24" wall thickness, "normal" exposure, Verts #9 @ 6.5"
RESULTS: fs = 32.21, Sd = 1.20 Mu = 163.0 kip-ft/ft and PhiMn = 168.1
24" wall thickness, "severe" exposure, Verts #9 @ 5.5"
RESULTS: fs = 28.81, Sd = 1.34 Mu = 182.2 kip-ft/ft and PhiMn = 196.5
24" wall thickness, "severe" exposure, Verts #10 @ 6.5"
RESULTS: fs = 25.89, Sd = 1.49 Mu = 202.8 kip-ft/ft and PhiMn = 209.2
(Again, these are all hypothetical, just for the sake of discussing the fs, Sd and Mu calculation)
Thanks for considering.