Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

ACI 7.10.5.3 explanation needed

Status
Not open for further replies.

CTW

Structural
Joined
May 30, 2002
Messages
312
Location
US
I need some help fully understanding what this section is describing. I understand that every corner and alternate bar should have support provided by the corner of a tie, but I'm unclear about the 6" or less. Is 6" the max. spacing of bars when more than 4 are req'd by analysis? What if I had a column similar to the one shown in the figure with 12 reinf. bars, except my bar spacing was 7 or 8 inches. Would I need to add more steel to reduce the spacing?

 
You could either add column steel so that the spacing of adjacent bars is less than 6 inches or add ties so that each bar (with a spacing of more than 6 inches) is laterally supported. Even if you add column bars every other bar needs to be supported so you're probably ahead if you add ties.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top