Hi can Anyone please confirm me that there are no minimum cover to be applied on shear walls for fire protection?because ACI code seems not indicating such a requirement.it only talks about overall thickness.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
This may mean this requirement is covered elsewhere in other general building codes as far as the ACI compliance framework is concerned. So it is required, just not covered in ACI standard as I read it.4.11.2 Where the general building code requires a thickness of concrete cover for fire protection greater than the concrete cover specified in 20.5.1, such greater thickness shall govern.